| Posted: Mon Jan 26th, 2009 10:00 pm |
|
21st Post |
|
hvacdrd Fellow, Academy of Sublime Masters of Appliantology
|
RegUS_PatOff is the master of finding the documents - awsome. Looks like we are on the right track. That relay is identified as the IDR(induced draft relay) - after following the advice of Cactus Bob by turning the fan to see if it spins freely, you can try the jumper.
____________________ Tip Jar |
||||||||||||||
| |||||||||||||||
| Posted: Tue Jan 27th, 2009 12:41 am |
|
22nd Post |
|
papollonia Senior Apprentice Appliantologist
|
WOW!!! This is great... Thank you so much for the link to the manual... I was searching for it and could not find it... Yes that is the wiring diagram on page 14,, I just compared them and that is indeed it is.. Is that relay a part that i can buy?? Being a non HVAC guy??? If it is cheap enough I may just buy it and replace it... There is a local appliance shop that will sell stuff to non hvac people... Thanks again for the advice
|
|||||||||||||
| ||||||||||||||
| Posted: Tue Jan 27th, 2009 12:46 am |
|
23rd Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
Did you check to see if the Relay is getting 24vAC to the Coil ? and if the Relay Contacts are closed (no voltage drop across Contacts) ?
____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
||||||||||||||
| |||||||||||||||
| Posted: Tue Jan 27th, 2009 12:49 am |
|
24th Post |
|
papollonia Senior Apprentice Appliantologist
|
Cactus Bob wrote: PAUL , sorry i was away today . it looks like your in good hands . that wireing photo is bad, cannot make out what goes where . jumping out the relay is a good idea . dont forget to power down the unit first , them jump , set thermostat for heat , then power on ...... you might want to just see if the little draft motor will turn with a little screwdriver .... Cactus Bob: Thanks for all your advice... If you are talking about the little fan on the bottom right? That does move freely, I did that Sunday...
|
|||||||||||||
| ||||||||||||||
| Posted: Tue Jan 27th, 2009 12:51 am |
|
25th Post |
|
papollonia Senior Apprentice Appliantologist
|
RegUS_PatOff wrote: Did you check to see if the Relay is getting 24vAC to the Coil ? No I did not, I have a slow day on Tuesday, if it is not pouring (like they are predicting ) I will check that... Thanks
|
||||||||||||||
| |||||||||||||||
| Posted: Tue Jan 27th, 2009 01:57 pm |
|
26th Post |
|
papollonia Senior Apprentice Appliantologist
|
" you can jumper the top two wires (terminals 2 & 4) and the motor should run. " WONDERFUL!!!!!!!!!!!!!! That worked the motor goes on when i jump the two!!!!!!! Now I need to find a local place that will sell me the new relay???? I will update you......................... Last edited on Tue Jan 27th, 2009 01:58 pm by papollonia |
|||||||||||||
| ||||||||||||||
| Posted: Tue Jan 27th, 2009 07:59 pm |
|
27th Post |
|
papollonia Senior Apprentice Appliantologist
|
Update: I got the relay!!!!!!!!!!!!!!!!!!!!! from a local appliance Parts House.. I will install it after the rain stops!!!Wednesday, but most likely Thursday.... Will let you know how it turns out... Again, I can not say enough thank yous to you guys.. Being self employed (thank Goodness my wife works )and two kids, to say money is tight would be a understatement
|
||||||||||||||
| |||||||||||||||
| Posted: Wed Jan 28th, 2009 09:20 pm |
|
28th Post |
|
papollonia Senior Apprentice Appliantologist
|
Ok... It stopped raining thsi afternoon.. I got the replacement relay, I check the spec's on the new relay with the guy at the supply house.. They all matched up.... See attached picture The only difference was the posts where in different postions but they where numbered, 1,2,3,4.. So I plugged the wires to there corresponding numbers... Checked them 4 times before powering up the unit.. Plugged the fuse in, I noticed the draft motor went on... ( like when I jumped the 2 wires earriler) Did not think anything was wrong... ( guess that was silly!! ) Went in and turned the t-stat to heat...and POP!!! sparks flew from the t-stat.. Turned it back off... Went back outside to the unit and the new relay blew out.. I took it out and it smells burnt and was warn.... I have a job to do that is take me past the supply house on Thursday,, I am goingto talk to them, could of sold me the wrong one??? I hope I did not demage anything??? Attachment: Relays.jpg (Downloaded 34 times) Last edited on Wed Jan 28th, 2009 09:21 pm by papollonia |
|||||||||||||
| ||||||||||||||
| Posted: Wed Jan 28th, 2009 09:32 pm |
|
29th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
It looks like in the original Relay (bottom picture) the (2) Coil terminals are on the left On the new Relay, Pin 1 is the Center = Orange/Orange Pin 2 is the Right = Black L1 Pin 3 is the Lower Left = Brown/Brown Pin 4 is the Upper Left Black Motor Last edited on Thu Jan 29th, 2009 02:12 am by RegUS_PatOff ____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
||||||||||||||
| |||||||||||||||
| Posted: Wed Jan 28th, 2009 10:16 pm |
|
30th Post |
|
Bobice Sublime Master of Appliantology
|
1-3 On both relays is coil (24V) The other two (2&4) is the power leads to the motor. When coil energizes these open contacts (2&4) close energizing the blower motor.
____________________ Retired US Army Refrigeration Specialist / NYC Board of Education HVAC/R (Retired) 40 Years HVAC/R service, sales,installations. |
|||||||||||||
| ||||||||||||||
| Posted: Wed Jan 28th, 2009 11:04 pm |
|
31st Post |
|
Bobice Sublime Master of Appliantology
|
Okay. The two Orange leads are the 24V leads. Connect one to terminal 1, the other Orange lead to terminal 3 on IDR Black from motor to terminal 4 on IDR Blue lead from motor back to T2 on contactor. Black lead from L1 on contactor to terminal 2 on IDR
____________________ Retired US Army Refrigeration Specialist / NYC Board of Education HVAC/R (Retired) 40 Years HVAC/R service, sales,installations. |
||||||||||||||
| |||||||||||||||
| Posted: Thu Jan 29th, 2009 01:39 am |
|
32nd Post |
|
papollonia Senior Apprentice Appliantologist
|
Ok I thought I did something wrong, I should not of connected the wires to the matching numbers from the old one to the new one.. Sorry my brain is sort of Jello tonight,, dealing with kids and HOMEWORK!!!! The old was like this: T1 = two orange wires T2 = Black wire from L1 T3 = Two Brown Wires T4 = Black from the Motor. Lets see if i have this correct: So on the new relay: The two Orange leads are the 24V leads. So these do not stay together on one connector. Connect one to terminal T1, The other Orange lead to terminal T3. Black from motor to terminal T4. Here is where i get confused!! There is no blue wire connected to the old one Did you mean the two Brown wires. Where do they go? Blue lead from motor back to T2 Black lead from L1 on contactor to terminal T2. Thanks
|
|||||||||||||
| ||||||||||||||
| Posted: Thu Jan 29th, 2009 01:53 am |
|
33rd Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
Bobice wrote: Okay. The two Orange leads are the 24V leads. Connect one to terminal 1, the other Orange lead to terminal 3 on IDRnot according to the Diagram yes, they should be the same pin numbers 1 & 3 are the Coil 2 & 4 are the Contacts 1 = Orange/Orange 3 = Brown/Brown 2 = Black L1 4 = Black Motor Last edited on Thu Jan 29th, 2009 02:02 am by RegUS_PatOff ____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
||||||||||||||
| |||||||||||||||
| Posted: Thu Jan 29th, 2009 02:01 am |
|
34th Post |
|
papollonia Senior Apprentice Appliantologist
|
Sorry for being so thick headed here!! So you are saying to connect whatever was connected from the old one to the new to the same numbers 1 to 1, 2 to 2, 3 to 3, 4 to 4? I did that and it burned out... Should i just try to buy the original one " 90-360 thru 90-486 WR/RBM TYPE 184 "
|
|||||||||||||
| ||||||||||||||
| Posted: Thu Jan 29th, 2009 02:04 am |
|
35th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
are you sure you had the right location of the pin numbers on the new Relay ?
____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
||||||||||||||
| |||||||||||||||
| Posted: Thu Jan 29th, 2009 02:05 am |
|
36th Post |
|
Bobice Sublime Master of Appliantology
|
IDR in your early post shows Orange on terminal 1 and Brown on terminal 3 Black lead from motor to terminal 4 on IDR. Other motor lead (whatever color) to T2 on Contactor. From L1 on Contactor black (or whatever color) to terminal 2 on IDR From page # 14 of manual downloaded Last edited on Thu Jan 29th, 2009 02:08 am by Bobice ____________________ Retired US Army Refrigeration Specialist / NYC Board of Education HVAC/R (Retired) 40 Years HVAC/R service, sales,installations. |
|||||||||||||
| ||||||||||||||
| Posted: Thu Jan 29th, 2009 02:12 am |
|
37th Post |
|
papollonia Senior Apprentice Appliantologist
|
Ok here is a picture of the two: The old one is on the Left.. The new one is on the right... Attachment: Close up of both relays.jpg (Downloaded 29 times)
|
||||||||||||||
| |||||||||||||||
| Posted: Thu Jan 29th, 2009 02:17 am |
|
38th Post |
|
Bobice Sublime Master of Appliantology
|
Terminals 1 and 3 on both relays are the coil. I just re-read the schematic and as I said the way I last posted is how it is wired.
____________________ Retired US Army Refrigeration Specialist / NYC Board of Education HVAC/R (Retired) 40 Years HVAC/R service, sales,installations. |
|||||||||||||
| ||||||||||||||
| Posted: Thu Jan 29th, 2009 02:37 am |
|
39th Post |
|
papollonia Senior Apprentice Appliantologist
|
Bobice: Thanks.. That is the way I had it wired, when it blew.. Orange/Orange on terminal 1 Brown / Brown on terminal 3 Black lead from motor to terminal 4 Other L1 Black motor lead to T2.. I wonder if it could of been a bad relay out of the box?
|
||||||||||||||
| |||||||||||||||
| Posted: Thu Jan 29th, 2009 03:06 am |
|
40th Post |
|
Bobice Sublime Master of Appliantology
|
T2 ? you do mean terminal 2 on the relay correct
____________________ Retired US Army Refrigeration Specialist / NYC Board of Education HVAC/R (Retired) 40 Years HVAC/R service, sales,installations. |
|||||||||||||
| ||||||||||||||