| Posted: Tue May 6th, 2008 10:18 am |
|
1st Post |
|
Walrus Senior Apprentice Appliantologist
|
We just moved in to our new house back in December of last year. We had a thunderstorm a couple of weeks ago and several items in my house got fried. Most importantly to us living here in Texas with summer coming is of course both air handlers upstairs seem to have been damaged. Both units outside seem to be working fine. When I turn on the T-Stat they kick in and if I go upstairs I can hear the hissing sound that tells me that they are doing their thing. The problem is that the fans in the air handlers do not kick on. I of course called to try and get warrenty work on the units, but when they came out and looked at them they said it was an "act of nature" and is not covered by the warranty. The told me at the time that the issue was the "fan control board". Being somewhat competent I thought "hey I can fix that rather than pay out $375.00". I ordered the board the part number for it was HK61EA010 and it came in. I replaced the board, of course after turning of the master switches for the unit. Then I attempted to turn the unit back on. I got nothing.
|
||||||||||||||
| |||||||||||||||
| Posted: Tue May 6th, 2008 11:07 pm |
|
2nd Post |
|
dkpd1581 Sublime Master of Appliantology
|
Start with the basics. Get your meter out and verify that you have your supply voltage (either 120 or 208/230 VAC) to the unit. Verify that you have 24VAC out of the transformer. Verify that you have no grounded wiring on any of the motor leads and that there is at least continuity between the common and other speed taps for the motor. Verify that the capacitor is within 10% of the listed value. Once the basics are covered, then got to the T-stat put FAN to "ON" and then verify 24 VAC from the T-stat to the control board terminal on the G (or fan) terminal and then verify that the high volts are coming out of the board to the motor lead terminals. Doing this will clear the breaker, fuses, transformer, board, T-stat, and motor. Even if you dont own a meter or know how to use one, go to the T-stat and turn the FAN to ON and HEAT/COOL to OFF and see if the blower motor at least spins up. See if there is at least a light or display on the board telling you that you are getting power to it. Write back and let us know and we will go from there.
____________________ Take a minute to visit me at: https://sites.google.com/site/dkpd1581/ |
|||||||||||||
| ||||||||||||||
| Posted: Wed May 7th, 2008 04:22 am |
|
3rd Post |
|
Cactus Bob Sublime Master of Appliantology
|
what control board did you replace ? you have two , one in in the air handler(never goes bad) and the one on the blower motor (allways goes bad ) ?
____________________ SORRY ABOUT THE SPELLING , I FIX GREAT , I DON'T SPELL WELL |
||||||||||||||
| |||||||||||||||
| Posted: Wed May 7th, 2008 09:55 am |
|
4th Post |
|
Walrus Senior Apprentice Appliantologist
|
First of all thanks for responding. Here is where I am at. I have not hooked up a voltmeter to anything yet, but I have checked from the T-Stat as you recommended. With the T-stat set to "off" and the fan only, set to "on", the fan does not spin at all. I also hear the "humming" inside the air handler during this, which a I am taking for power getting to the air handler. When I do turn the T-Stat to cool and the fan to on I have the unit outside turning on and the fan starting as well as a hissing sound, that I take for the cool air coming in at the air handler. I also hear an electric type humming when the power is turned on to the air handler in this fashion. I am pretty sure that the voltage is getting to the air handler. I am also feeling pretty confident that it is not the 24 VAC stuff since my outside unit is running well and the T-stat seems to be doing it's thing just fine. Next issue, I took a good look last night and can't seem to locate a capacitor for the motor. Is it inside the drum in this unit with the motor? Do I have to take the motor out to get at the capacitor? Thanks for your help.
|
|||||||||||||
| ||||||||||||||
| Posted: Wed May 7th, 2008 09:57 am |
|
5th Post |
|
Walrus Senior Apprentice Appliantologist
|
Thanks for responding. I replaced the one in the air handler, which did not appear to be burned or anything, but that is what the tech, I thought, told me was bad. The board you are referring to is with the motor? So do I have to pull the motor out of the unit to get at it? I also cannot locate a capacitor on this unit visually right now. I am thinking I have to take the motor out of its protective "cage" in order to check for the capacitor.
|
||||||||||||||
| |||||||||||||||
| Posted: Wed May 7th, 2008 12:50 pm |
|
6th Post |
|
Cactus Bob Sublime Master of Appliantology
|
OK . FIRST i hate to do this but the tech here that told you to do tests is wrong with the system you have . you have no cap you cant check 24 volts ect , ect , what you have is GE varable speed motor and theres no way to check them . there is a test box we have but you buying one just for one repair NO! ,BIG $$$$$ the board thats bad is part or is bolted to the back of the blower motor on the older ones it is replaceable on the new ones its not and you will need a motor depending on the motor it costs 300.00 to 900.00 so if you dont know what you are doing dont mess with is you can ruin it . the repair guy that came to your house was wrong ( i made this mistake once years ago , i learned fast . it was a costly mistake for ME ) i think you should step back and call carrier , or use a phone book and get factory service . you have a lot of money to loose and without the proper test equipment your gessing and so is your old repair guy ... so do no more tests , you cant see anything anyway the signals are digatal . the motor is DC ! bite the bullet and GET it fixed ..... good luck
____________________ SORRY ABOUT THE SPELLING , I FIX GREAT , I DON'T SPELL WELL |
|||||||||||||
| ||||||||||||||
| Posted: Wed May 7th, 2008 02:13 pm |
|
7th Post |
|
Walrus Senior Apprentice Appliantologist
|
|
||||||||||||||
| |||||||||||||||
| Posted: Wed May 7th, 2008 02:18 pm |
|
8th Post |
|
Pegi Fellow, Academy of Sublime Masters of Appliantology
|
Lightning causes damage to anything if it gets a hit, everyone should know this. Damage like this is not ever covered under warranty. This goes under your homeowners insurance, have you contacted them yet???
____________________ Moderator & Assistant Admin. for Servicetechhelp Associaton, Inc. http://www.servicetechhelp.com STH HELPDESK URL.... http://www.servicetechhelp.com/h2desk/ ___________________________________ For Gordon... http://serviceeveryday.com/ |
|||||||||||||
| ||||||||||||||
| Posted: Wed May 7th, 2008 03:23 pm |
|
9th Post |
|
Cactus Bob Sublime Master of Appliantology
|
did YOU tell them you had lightning ? nobody tells ME i have these motor going bad all the time , i cant tell what killed them . a call comes in . we go out fix it . take the motor back to our supplyr fax a labor form , get paid ... done..... nobody asks anything more .. .. so think about what your doing and saying . ... it might be to late allready carrier might have FLAGED your unit .... but thay might not have also
____________________ SORRY ABOUT THE SPELLING , I FIX GREAT , I DON'T SPELL WELL |
||||||||||||||
| |||||||||||||||
| Posted: Wed May 7th, 2008 05:03 pm |
|
10th Post |
|
Walrus Senior Apprentice Appliantologist
|
The problem is they are located not far from us and they knew about the lightning storm, then I have two units, one for upstairs and one for down. Both are out. I guess to them that was pretty conclusive evidence that the storm caused the problem. So is it not possible for me to replace this motor? I looked at the bottom of it and it seems to just have one connector that attaches the power to the bottom and then there is a four legged bracket that seems to hold it in place. If I pulled it and ordered the motor what is to keep me from replacing it myself. I did call a Carrier representative and he said that they would probably be willing to replace the fans, but I would have to deal with the service company about the hours. As far as insurance goes, my homeowners policy, like most has a deductible that is 1% of the cost of my house. That is my deductible is $3,700.00 so my insurance is not a lot of help in this situation.
|
|||||||||||||
| ||||||||||||||
| Posted: Thu May 8th, 2008 12:28 am |
|
11th Post |
|
Cactus Bob Sublime Master of Appliantology
|
whats to keep you from reparing it your self ? NOTHING but .........what if i am wrong ?
____________________ SORRY ABOUT THE SPELLING , I FIX GREAT , I DON'T SPELL WELL |
||||||||||||||
| |||||||||||||||
| Posted: Thu May 8th, 2008 10:10 am |
|
12th Post |
|
Walrus Senior Apprentice Appliantologist
|
Thanks Cactus, I believe I am going to pull this motor and see what the model number is and go from there. I wish I had someone who I could trust to come out and look at the system for a reasonable rate and I could feel sure they would not try and gouge me on parts and labor, but these days people will replace a fuse and charge you for a motor. That is why I try and do everything myself as much as possible. I am sure there will be more to follow.
|
|||||||||||||
| ||||||||||||||
| Posted: Thu May 8th, 2008 02:18 pm |
|
13th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
SearsParts Direct shows the motor model part number as HD42AE231 in the CABINET PARTS section, and Sears says "Contact Customer Support for Availability" 800-252-1698, and I can't find anything else on the web.
____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
||||||||||||||
| |||||||||||||||
| Posted: Thu May 8th, 2008 04:01 pm |
|
14th Post |
|
Walrus Senior Apprentice Appliantologist
|
RegUS, I called the number and they could not find the part. They said that the system did not give them any information on the part like price. Man, this is really a pain. Thanks for your assistance though!
|
|||||||||||||
| ||||||||||||||
| Posted: Tue May 13th, 2008 04:26 pm |
|
15th Post |
|
Walrus Senior Apprentice Appliantologist
|
Thought I would update. I found the part at this website. http://www.expertappliance.com/carrier-heating.html I bought the first one and installed it and now I have A/C downstairs!!
|
||||||||||||||
| |||||||||||||||
| Posted: Wed May 14th, 2008 12:13 am |
|
16th Post |
|
Cactus Bob Sublime Master of Appliantology
|
Last edited on Wed May 14th, 2008 12:41 am by Cactus Bob ____________________ SORRY ABOUT THE SPELLING , I FIX GREAT , I DON'T SPELL WELL |
|||||||||||||
| ||||||||||||||